Model removal of air from a zone to Exhaust

asked 2015-06-11 09:53:18 -0500

tajjmann's avatar

updated 2015-07-12 14:17:51 -0500

I have a model with a Chiller hooked to 2 Air Handler Units as depicted in the schematic below. How do i model the removal of air (50% and 80%) from each zone through to the Exhaust in OpenStudio.image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2015-06-12 03:30:22 -0500

updated 2015-06-12 03:30:58 -0500

In the case depicted, the easiest is to use a separate AirLoopHVAC for each AHU/Zone combination.

By default, E+ assumes that the ventilation is balanced, so the supply to your zone is the exhaust from your zone. Considering this, you just need to say that for AHU 1 you want 50% of outside air, and automatically 50% will be relieved (exhausted to the outside).

This will be done in the Controller:OutdoorAir attached to the AirLoopHVAC:OutdoorAirSystem.

Outdoor Air Controller

Think carefully about how your unit is actually working:

  • Is it constant volume or variable volume?
  • If variable volume, do you want the outside air to be 50% of whatever the flow is at that moment, or do you always want a fixed amount like X m3/s or CFM?

  • If you always want X CFM, just fill the Minimum Outdoor Air Flow Rate. (Or if you have specified the correct DesignSpecification:OutdoorAir, you could let it as autosized)

  • If you always want X %, play with Minimum Fraction of Outdoor Air Schedule

You can always add a return fan on your AirLoopHVAC to account for this fan power (see picture above, I have one on the return), though remember it will handle the return air, not just the relief air (but your AHU handles the difference between the two, so you can always do a weighted average of fan power).


One other way would be to use a Fan:ZoneExhaust, but it'll be more complicated and not worth it in your case considering your airflow is coming from an AHU and is balanced. (In OpenStudio under the Thermal Zones tab, you add Fan:ZoneExhaust in the Zone Equipment Column. You won't see it under the HVAC system tab.)


PS: the schematic is slightly confusing, it makes it look like the chiller is part of the air loop. Here you only want to deal with the airflow so you could just exclude it.

edit flag offensive delete link more

Comments

To add to Julien's answer, just replace his single speed coils with a Coil:Cooling:Water and connect it to a plant loop with chiller.

MatthewSteen's avatar MatthewSteen  ( 2015-06-12 09:06:15 -0500 )edit

Thanks Julien Marrec, where do I find DesignSpecification:OutdoorAir?

tajjmann's avatar tajjmann  ( 2015-06-12 09:24:53 -0500 )edit

@MatthewSteen: I didn't think about putting a screenshot relevant to the chiller situation, good point.

@tajjmann : Multiple places: Space Type and Facility. Typically you should specify it at the Space Type level and then just assign your spaces to said space type (makes more sense). By the way, mark the answer as accepted if you're satisfied so we can close the topic.If not satisfied, let us know what's missing so someone can take a shot at it.

Julien Marrec's avatar Julien Marrec  ( 2015-06-15 05:40:49 -0500 )edit

Sorry Julien: I couldn't figure a way around marking the answer as accepted. Finally done. Thanks foe the assistance.

tajjmann's avatar tajjmann  ( 2015-06-15 11:07:08 -0500 )edit

Hello @Julien Marrec, I need to specify "X % of outdoor", could you elaborate on how to do that in "Minimum Fraction of Outdoor Air Schedule"?

tajjmann's avatar tajjmann  ( 2015-06-22 09:58:32 -0500 )edit