My HAVC system cools down slower and slower

asked 2022-07-22 09:30:14 -0600

XiaoMA's avatar

updated 2022-07-25 12:28:22 -0600

Hello guys, I met a problem while implementing a simple model which cools down the 30 degrees environment to 20 degrees with a relatively realistic HVAC model (not using ideal air loads). But I found the temperature changed slower and slower. for example, changed 2.34 degrees in the first 10 mins, and 1.26 in the next 10 mins, and less and less.

My HVAC is very simple, it only has a coil cooling device with a Total Cooling Capacity of 20000W and a constant volume fan.

If you have any idea about this or need more information, please tell me. Thank you for your help!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2024-06-27 09:40:05 -0600

XiaoMA's avatar

This is actually because of something called thermal inertia. Materials such as walls and furniture absorb or release heat slowly.