Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

OpenStudio Application: Server Room Modeling

asked 2022-05-12 23:52:44 -0500

nissaldeelaka's avatar

updated 2022-05-13 08:33:23 -0500

Hello,

I have a server room in the building I'm modeling. I've been using the IT Room schedule from the BCL. However, the cooling load is lower than in the Computer Room Air Cond. Unit (CRAC) in the actual building. I believe this is because the server equipment continuously generates heat and the CRAC unit works all the time. How do I go about this? How do I create a heat generator?

Thanks in advance.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2022-05-16 01:56:02 -0500

Put a higher load in the zone. Such as an ElectricEquipment or an ElectricEquipment:ITE:AirCooled.

If you take ElectricEquipment, pay attention, in addition to the wattage, to the Fraction Radiant, Fraction Latent, and Fraction Lost fields. Read carefully the section titled Heat Gains from Electric Equipment

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2022-05-12 23:52:44 -0500

Seen: 161 times

Last updated: Aug 25 '22