Thermal Loads inside Open Studio and Energy Plus Results

asked 2 years ago

enriquesissa's avatar

updated 2 years ago

Hi Everyone,

In the Open Studio result *.HTML, I get a big difference between the load calculations and the system size. Almost double. I need to clarify that the model doesn’t have any ventilation/economizer or infiltration rates ( For testing proposes). Using SZ Heatpump my open studio output defines some Minimum and maximum Outdoor air. Why there is a Maximum if everything is set to zero. This is possible to view "Controller:OutdoorAir" (https://drive.google.com/file/d/1fKjk...)

Also, the load is specified as hardcoded. I would like to understand better the source of this number and how it gets calculated.

Thanks!

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
2

answered 2 years ago

The sensible table only shows sensible loads associated with the space. The HVAC system sizing can include outside air loads, fan heat loads, efficiency penalties, latent heat loads, standby losses, and parasitic loads.

Also see this thread: https://unmethours.com/question/60419...

Preview: (hide)
link

Comments

But double the sensible? I defined zero infiltration or Outdoor air. Also Is there any way to see the breakdown?