Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Thermal energy storage Chilled Water Tank With multiple chillers

asked 2021-10-21 12:56:43 -0600

Draza's avatar

updated 2021-10-21 13:21:33 -0600

I am modeling a central chilled water plant with a stratified chilled water thermal storage device in OpenStudio. There are multiple chillers in the central plant. My question is how would I set up the tank to be able to be charged by multiple chillers within the plant loop? According to the plant application guide, the TES tank should be placed on the outlet of the chiller object, if I do this then only that chiller is able to charge the tank. My thought was to either: 1. Create two separate loops. The first loop would have the chillers on the supply side and the TES tank on the demand side. the second loop would have the TES tank on the supply side and the load on the demand side. Is there any drawbacks to this? 2. Use multiple TES tank objects with smaller capacity on the outlet of each chiller. This doesn't seem like a good workaround but I don't see another way to model the TES Tank with it being connected to multiple chillers.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2022-10-21 04:45:29 -0600

Hello, Do you try to use a splitter and a mixer? It would be like using a bypass. You can look at the absorption.idf in energyplus examples files. There is an example of one cooling tower used by two chillers and they did it like this.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-10-21 12:56:43 -0600

Seen: 178 times

Last updated: Oct 21 '21