Show Tempering Valve as connector

asked 2021-09-06 23:14:24 -0600

RMurray's avatar

updated 2022-02-18 17:00:43 -0600

How do I show a tempering valve in a plant loop using EnergyPlus? I can't add it to the connector list, so I'm at a loss. Thanks!

edit retag flag offensive close merge delete

Comments

1

Please use existing tags and tag your question with the software you're using (EnergyPlus?)

Julien Marrec's avatar Julien Marrec  ( 2021-09-07 07:44:18 -0600 )edit

I've tried several times to edit the tags to no avail.

RMurray's avatar RMurray  ( 2021-09-07 10:22:15 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
3

answered 2021-09-09 06:47:18 -0600

Have you looked at the E+ example files? HP_wICSSolarCollector.idf and SolarCollectorFlatPlateWater.idf are the two that use TemperingValve (this is a link to the I/O reference guide, you need to read that too).

It needs to be put on its own branch, the other only branch would be the one with your WaterHeater:Mixed object (no bypass or anything else)

edit flag offensive delete link more

Comments

1

Also, the ConnectorList object in EnergyPlus is just looking for the splitter & mixer on the supply or demand side of the plantloop. As Julien mentioned, the TemperingValve is on a branch between the splitter & mixer.

Aaron Boranian's avatar Aaron Boranian  ( 2021-09-09 09:10:24 -0600 )edit

Thanks to both Julien and Aaron!!

RMurray's avatar RMurray  ( 2021-11-04 15:35:53 -0600 )edit