Operation of Parallel Fan-Powered VAV during cooling

asked 2021-08-08 02:35:33 -0600

Keigo's avatar

updated 2021-08-08 02:37:39 -0600

When complying with ASHRAE 90.1 Appendix G, should we turn off Zone PIU Fan during cooling? Or should we keep it running all the time?

Appendix G specifies VAV with PFP boxes as HVAC system of baseline model for Large nonresidential buildings in climate zone 0 to 3A (hot or warm&humid climate), and it also specifies the airflow of the parallel fan in PFP box. The airflow of the parallel fan is constant.

image description

image description

On the other hand, 90.1-2016 User's Manual shows the following figure and suggests that the parallel fan in PFP box should be turned off during cooling.

image description

I think this Figure 6-V is correct. But if so, since buildinigs in climate zone 0 to 3A has no or less heating mode, the parallel fan is off almost all year round. There is no point in setting airflow and fan power of the parallel fan in accordance with Appendix G. I don't understand why ASHRAE specifies System 6 or System 8 as HVAC systems in hot climate zones.

image description

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
3

answered 2021-08-24 03:53:03 -0600

Keigo's avatar

Self-resolved. ANSI/ASHRAE/IES Standard 90.1-2016 Performance Rating Method Reference Manual provides the following explanation.

image description

The Parallel Fan should be off throughout cooling.

From now on, I will refer to the Performance Rating Method Reference Manual first.

edit flag offensive delete link more

Comments

Hi Keigo, If the terminal unit fan is kept OFF, I wonder how the software will proceed with further simulation in first place. Since the primary airflow through AHU gets distributed mostly through the terminal units. Can you clarify this? Also, did you find this applicability for both ASHRAE 90.1 2010 & 2016? Appreciate your response.

Anurag_G's avatar Anurag_G  ( 2025-06-25 01:07:16 -0600 )edit
1

This post is about "Parallel" fan-powered VAV terminal unit. The terminal unit fan is for "recirculation" only. The primary air is supplied to each zone even if the terminal unit fan is off. Of course, this applies to all versions of ASHRAE 90.1.

Keigo's avatar Keigo  ( 2025-06-25 02:25:03 -0600 )edit

Hi Keigo, I am sorry I misinterpreted the concept earlier. The minimum volume setpoint of 30% for the parallel fan powered box still remains valid for cooling, right? Also, does the reheat coil remain ON throughout the annual simulation?

Anurag_G's avatar Anurag_G  ( 2025-06-25 02:59:51 -0600 )edit
0

answered 2025-10-24 03:40:40 -0600

Anurag_G's avatar

Hi Keigo, I am sorry to open this thread once again. While working on a baseline case following system 8 (appendix G ASHRAE 90.1 2010), there is a requirement for PFP terminal unit. Now I have a couple of queries regarding that: 1. Whether the PFP terminal units are applicable to all zones or only the zone toward the perimeter of the building? 2. We are working on design builder, so there are couple of parameters in PFP box which I am unsure of to input. Parameters like Fan On flow fraction, Maximum primary air flow rate(m3/s), maximum secondary air flow rate(m3/s), and minimum primary air flow fraction. These are currently autosized. Can you help me out in this. Appreciate your help and way forward.

edit flag offensive delete link more

Comments

@Anurag_G since this is a follow-up question instead of an answer to the original post, please leave this text as a comment (either under Keigo's self-answer or question) and then delete this answer post. There is a 600-character limit for comments, so you will have to split this across multiple comments.

Alternatively, you can also create a new question post for your question, and leave a link to reference this post for others to review.

Aaron Boranian's avatar Aaron Boranian  ( 2025-10-24 09:54:16 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Question Tools

2 followers

Stats

Asked: 2021-08-08 02:35:33 -0600

Seen: 1,167 times

Last updated: Oct 24