eQUEST Can I set a triggering temperature for heating

asked 3 years ago

Tim123's avatar

Dear eQUEST users,

I am modeling based on the assumption that heating will be provided only when the outdoor temperature is lower than 10 degree C with a 20 degree C design heating temperature. So, how can I make such input? Many thanks.

Regards, Tim

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
0

answered 3 years ago

You can use a schedule of type RESET to connect the operation of heating equipment to the outdoor air temperature. If you also want the indoor air temperature to be used as a setpoint control, you may be able to use a thermostat to control the heating in the zone (by e.g. baseboards or fan coils), and connect the zone heating equipment to a hot water loop that uses a loop operation mode of “SNAP”. I.e. go to the Water-Side HVAC tab, select the Hot Water Loop and double click to open the “Circulation Loop Properties” Window. In this window go to the Operation tab, and under Loop Operation select Snap. For the Snap Location set Outdoor and for the Snap Temp set 10°C (or equivalent value in °F). This will turn off the HW loop above 10°C outdoor air temperature.