First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

VRF System always failed to run

asked 3 years ago

shmily_world's avatar

updated 3 years ago

Has anyone encountered this problem: the model is normal with ideal air load or other HVAC system, but when replaced by VRF system, the simulation will always failed? C:\fakepath\微信截图_20210708104732.png C:\fakepath\1.png

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
3

answered 3 years ago

"...invalid Heating Energy Input Ratio Modifier Function of Low Part-Load Ratio Curve Name = VRF SYSTEM HEATIINGEIRLOWPLR 13 has out of range value. Curve minimum value of X = 0.500 must be <= Minimum Heat Pump Part-Load Ratio =0.250." The error file tells you what is wrong - your curve is under-defined. The heat pump can go do to a part load ratio of 0.250, but one of your curves is only specified down to 0.500. So it can't get curve values for X values between 0.25 and 0.5. Try to regenerate your equipment curves or find another source for them for the full range available to the equipment, in this case down to a part load ratio of 0.25.

Preview: (hide)
link

Comments

That's quite helpful! Thx a lot!!

shmily_world's avatar shmily_world  ( 3 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 3 years ago

Seen: 227 times

Last updated: Jul 31 '21