Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

French renovated buildings

asked 2014-10-18 05:01:28 -0500

Theo's avatar

updated 2017-05-04 13:44:25 -0500

Hi, residential existing buildings in France (H3) take major renovations (walls, ceilings, floors, airtightness, MV) do they have to fulfill some minimum requirements (U values, or total heating demand)? Can you provide me these values with a reference?

edit retag flag offensive close merge delete

Comments

Since we don't have a meta site, I'll ask it here. Should we add a "code" tag for code-related questions or something like that? (@Amit Roth, @Neal Kruis)

Julien Marrec's avatar Julien Marrec  ( 2014-10-21 07:51:33 -0500 )edit

@Julien Marrec I added the 'code-compliance' tag. 'code' is way to general, especially in the software world.

Neal Kruis's avatar Neal Kruis  ( 2014-10-22 11:41:15 -0500 )edit

Neal, that's a very good point. code-compliance it is.

Julien Marrec's avatar Julien Marrec  ( 2014-10-23 04:57:59 -0500 )edit

1 Answer

Sort by » oldest newest most voted
1

answered 2014-10-21 07:35:42 -0500

updated 2014-10-21 07:41:14 -0500

Your building will potentially fall under the existing building thermal regulation called "RT Existant" (RT stands for Réglementation Thermique). In order to determine whether you need to abide by it, you need to know whether you will need a work permit or not. Considering you said it's a major renovation, I'm going to assume yes.

Under the "RT Existant", there are two paths:

  • "RT élément par élément": this is a prescriptive by element path. For each element you are affecting, you will need to match a specific performance criteria (called "garde-fous" <> safeguards). Eg: if you are replacing the wall insulation, the R-value needs to be higher than 2.3 m².K/W (except exceptions). If you are replacing a boiler, you will need an efficiency higher than a specific value.

  • "RT globale": this is both a prescriptive by element and a global performance path. Each element you will change (and only those) will have to meet the same specific performance criteria as above, BUT you will ALSO have to demonstrate a performance for the building as a whole. Using a specific calculation methodology (see [1]), you will need to demonstrate that you are below a specific consumption in source kWh/m².year that matches both your climate (location) as well as the type of heating system you have (that's for residential, for commercial it's 30% below baseline). You'll also need to check that a summer indoor temperature is below a reference temperature (that varies a lot too).

In order to determine whether you fall under one or the other: Flow chart to determine under which RT you fall under

  • If your building is smaller than 1000 m² you're under "RT par élément"
  • If your building is larger than 1000 m² but the cost of the work is lower than 25% of the value of the building (value being defined in a specific way and not representative of its costs on the market), you're under "RT par élément"
  • If your building is larger than 1000 m², the cost of the work is higher than 25% of the value of the building, but the building was built before 1948, you're also under "RT"
  • Basically, the only way you're under "RT globale" is if your building is larger than 1000 m², the cost of the work is higher than 25% and the building was built after 1948

see: Site RT Bâtiment (in french)

[1] Note about the calculation methodology: this is a normative calculation. IT DOES NOT REPRESENT THE REALITY OF HOW YOUR BUILDING IS USED. The idea is that all entry parameters are pre-defined: occupancy, indoor temperature, etc. It allows apple-to-apple comparison of two buildings but completely forgoes the intended usage. If for a given reason you know right from the start that a given building will be used at indoor temperatures of 24°C in the winter for example, you could end up making bad choices just to abide by the law... This doesn't tell you how much you will actually ... (more)

edit flag offensive delete link more

Comments

Very interesting to see how things are done in other countries!

__AmirRoth__'s avatar __AmirRoth__  ( 2014-10-21 07:41:22 -0500 )edit

France does a lot of interesting things and the code (for NC at least) is fairly stringent compared to the US (for residential it's pretty close to Passivhaus standards right now), but that calculation methodology I really have problems with... It's so important I had to mention it. Unfortunately, lots of people are even doing "energy audits" and show some projected savings over 5, 10 or even 20 years based on this calculation methodology which doesn't represent reality one bit.</rant>

Julien Marrec's avatar Julien Marrec  ( 2014-10-21 07:48:11 -0500 )edit

Thanks a lot. Really helpful !!! Do you have any more information for RT ex related with the minimu R values for walls, ceiling, floor, window (ggl) and infiltration?

Theo's avatar Theo  ( 2014-10-23 02:21:06 -0500 )edit

That's a comment, not an answer. In order to answer your comment, do you read french or not?

Julien Marrec's avatar Julien Marrec  ( 2014-10-23 04:58:52 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2014-10-18 05:01:28 -0500

Seen: 197 times

Last updated: Oct 23 '14