I am trying to model a parallel branch for HeatPump and Furnace. But i am not sure how to connect them in EnergyPlus. The diagram is shown here. image description Is there any documents describing the similar way? Thanks.

edit retag flag offensive close merge delete

Comments

@Aaron Boranian I believe that is what @ep_user is looking for; at least that is how I interpreted the question. Would the branch connectors and nodes be the appropriate resource?

sashadf1's avatar sashadf1  ( 2021-06-18 12:43:25 -0500 )edit

@ep_user So you want a furnace (fuel heating coil) in parallel with heat pump (DX) coils that share one supply fan and serve one zone?

Aaron Boranian's avatar Aaron Boranian  ( 2021-06-18 12:48:06 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
0

answered 2021-06-18 13:38:54 -0500

sashadf1's avatar

look into https://bigladdersoftware.com/epx/doc....

It looks to me like you need a Splitter (Connector) object right after the Fan and before the Cooling Coil that splits the airflow driven by the single fan through the Branch with the clg, htg, and aux coil and the furnace Branch, and a Mixer (Connector) object right after the Aux heating coil that combines the flows from the furnace and coil branches. In terms of the IDF, you would specify the geometry of the loops with correct node assignments.

Per the documentation, "Nodes connect components along a branch: the outlet node of one component is the inlet node of the next downstream component."

The DualDuctAir example shows a configuration for one duct branch with heating and one duct branch with cooling. You want one branch with the coils and one branch with the furnace. Not sure if a DualDuctAir system is right for that configuration, but I hope this helps get you started.