Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

ResStock Autosizing Algorithm

asked 2021-06-11 15:50:13 -0500

sashadf1's avatar

updated 2022-10-20 15:54:51 -0500

ResStock v2.2.4 uses load calcs from Manual J along with Manual Sizing S procedures from ACCA to size HVAC.

When opening the IDFs generated by PAT, we noticed that the capacities and airflow rates for equipment in the IDFs were hard-sized rather than autosized. Even though ResStock was "autosizing," when the osm models generated by PAT were forward translated to E+ IDFs before being run on AWS cloud, the HVAC equipment in the IDF has hard-sized values. These capacity and airflow values are being calculated through the hvac_sizing.rb script (which codifies Manual J/S) rather than specifying E+ to autosize.

If I want ResStock to autosize for an 80 deg F cooling, heating, and dehumidification setpoint, what are the appropriate edits I need to make to hvac_sizing.rb?

I have implemented the following changes below, is that sufficient?

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2021-07-26 13:42:11 -0500

sashadf1's avatar

The purpose of this question was to get a simulation result with a constant zone temperature that matched the setpoint for all hours of the year. The best way to do this is with Ideal Air Loads Zone HVAC units, using this measure; https://bcl.nrel.gov/node/84744.

Be careful though; EMS objects and ResStock's default heating and cooling setpoints in Constants.rb must be rewritten in order for the measure to work as intended.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2021-06-11 15:50:13 -0500

Seen: 317 times

Last updated: Jul 26 '21