Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Economizer high limit doesn't work

asked 2021-05-08 15:54:40 -0600

Jim Dirkes's avatar

updated 2021-05-17 14:38:19 -0600

I don't normally have secondary limit on differential enthalpy economizers, but this model actually has two - an enthalpy value and a dewpoint. Setup seems simple, but it's not working.... EnergyPlus setup is:

image description

Results are:

image description

Insights, please!

ps, For the series of values shown, outdoor temp is ~29c, RH ~60%. Zone temp & RH are shown in the image (~20C, = 60%RH)

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2021-05-09 18:28:15 -0600

Jim Dirkes's avatar

I think the "High Humidity Control" was confusing things. I turned it off an now results are much improved.

edit flag offensive delete link more

Comments

Jim, another setting to watch out for is in the DesignSpecification:OutdoorAir object. Unless otherwise defined, E+ is using a default value for the outdoor_air_flow_per_person parameter, which can cause unexpected OA flow behavior if that value exceeds your min OA flow rate.

codybond's avatar codybond  ( 2021-05-10 09:17:02 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2021-05-08 15:54:40 -0600

Seen: 129 times

Last updated: May 09 '21