Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Thermostat and humidistat

asked 2021-04-19 04:10:26 -0500

wjsjch's avatar

updated 2021-04-19 04:10:54 -0500

In OS, to finish HVAC sizing, I only need to assign the thermostat schedule to the corresponding thermal zone instead of providing both thermostat schedule and humidistat schedule. But to describe a certain state of air, it needs both dry bulb temperature and relative humidity. And I'm sure that OS can't calculate the cooling/ heating load with just one parameter (dry bulb temperature).

So, I believe OS must have assigned a certain RH value to the thermal zone automatically. And my question is: what principle is OS based on when it automatically assigned an RH value to a thermal zone.

Looking forward to your reply!

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2021-04-19 13:50:41 -0500

updated 2021-04-19 13:53:20 -0500

OS does not automatically assign a humidity/RH setpoint. In many cases, and especially throughout California and much of the western/arid US, humidity is often neglected when designing HVAC systems. In these cases, only a dry-bulb temperature setpoint/schedule is necessary to specify in order to do a load calculation. Of course, there will be humidity, depending on the outside air moisture content, the amount of ventilation air supplied by the system, and internal source of moisture, but that does not make it necessary to control for humidity; it is perfectly acceptable to control for only dry-bulb air temperature, except perhaps for critical space types such as operating rooms and other spaces where humidity control is required. For example, all of the DOE/PNNL commercial prototype models do not control for humidity, except for a single zone in Outpatient Healthcare (Floor 1 Operating Room 1).

edit flag offensive delete link more

Comments

It's really interesting to know such a different design principle in the US. Thank you very much!

wjsjch's avatar wjsjch  ( 2021-04-19 19:45:04 -0500 )edit
1

answered 2021-04-20 11:05:15 -0500

Petros Dalavouras's avatar

Openstudio does not apply a humidistat in thermal zones automatically nor does it need to. Thermostats and humidistats are used only to control a specific variable of the air of the thermal zone. Thusly, if you only have thermostats your HVAC system will operate only to keep the temperature of the thermal zone between you setpoints, ignoring the humidity of the thermal zone. So to sum it up, Openstudio does have a specific state of air in each timestep but thermostats and humidistats are just control signals for your HVAC system. However, in order to calculate the airflow rates required for the thermal zone, openstudio uses the parameters you inputed in thermal zones for supply air which among others is the supply air temperature and humidity ratio.

image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2021-04-19 04:10:26 -0500

Seen: 433 times

Last updated: Apr 20 '21