Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Setting up the HVAC for a building model

asked 2021-03-16 09:24:42 -0500

Ahmad's avatar

updated 2021-03-22 11:36:45 -0500

Hello,

I am new to Openstudio and I'm working on modeling the HVAC for an offices building and I would appreciate guidelines on how to do that. It is hard for me to know which system to choose in the HVAC tab in Openstudio and how to reflect the existing network.

The building has 4 major AHUs in the basement (1 that is associated for an auditorium and 3 for the rest of the building). These 4 major AHUs have a supply fan section, a water cooling coil section, and a water heating coil section. There are two chillers for the cold water (1 as a backup for the auditorium) and a heat exchanger is coupled from another building for the hot water. Each floor has AHUs in main areas such as entrances, corridors, .. and each room has a FCU.

Many thanks in advance.

With my best regards to all the team

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2021-03-18 19:03:45 -0500

mattkoch's avatar

The OpenStudio Application has several tabs on the left edge, each tab with an icon representing what the tab does. From the top, they are Weather, Schedules, Constructions, Loads, Spaces Types, Geometry, Facility, Spaces, Thermal Zones and HVAC, followed by a few others. The HVAC tab has two rectangular arrows stylizing a loop. Click on that tab.

Now you'll see a screen that has a green "+", a blue "x2" and a red "x" on the top left. Click on the green "+". In the dropdown that follows, select "Empty Air Loop". You'll see an empty air loop with five little circles (open dots, really) - these are where you will add coils and fan. The number of these dots will change as you manipulate this loop.

Now on the right of the screen, page down to "Coil Cooling Water", click on that, select "CHW Clg Coil" and drag that to the top right small circle. Then, on the right of the screen again, page down to "Coil Heating Water", click on that, select "HW Htg Coil" and drag that to the top right small circle (again). Then, on the right of the screen once gain, page down to "Fan Variable Volume", click that, select "Var Spd Fan" and drag that to the top right small circle (once again). You have now created an AHU with CHW cooling coil, HW heating coil and constant speed draw-through fan. If you need a blow-though fan instead, drag a new "Var Spd Fan" to the top left small circle instead, then click on the black "x" by the existing fan to delete that. if you have thermal zones already, you can drag them to the bottom center small circle.

Now on the top of the screen, there is a selection box that should read "Air Loop HVAC 1". That's the name of your AHU, for now.

Now, click back on the green "+" on the top left and this time select an "Empty Plant Loop". Similar to what you did on the air loop, you can now add a chiller to the top center dot. And, if instead of leaving the right hand side on "Library" you select "My Model", you can drop down to "Coil Cooling Water", select "CHW Clg Coil" and drag that to the bottom center dot. While you are still in the plant loop, also add a pump (you need to go back to the "Library" tab), page down to "Pump Variable Speed", select "Var Spd Pump" and drag that to the top left dot. Obviously, you can/must/will create another plant loop for the boiler.

This is just one of many ways to skin that dog, and it is by no means complete. You still need to add setpoint managers to all loops, you might want to add an OA system and and a heat recovery wheel to the air loop, etc. I am just aiming to get you acquainted (with OpenStudio 2.9.1). Important: The "Library ... (more)

edit flag offensive delete link more

Comments

Mattkoch, thank you very much ! I really appreciate the detailed steps and I will make sure to take everything into consideration.

Ahmad's avatar Ahmad  ( 2021-03-19 08:12:07 -0500 )edit
1

In another post, someone used a Four Pipe Fan Coil, so you can use that for your FCU. But note that these are added as zone equipment on the thermal zones tab, not in air loops on the hvac tab.

mattkoch's avatar mattkoch  ( 2021-03-19 22:27:20 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2021-03-16 09:24:42 -0500

Seen: 376 times

Last updated: Mar 18 '21