Zone load variation between E+ input and output

asked 4 years ago

Jim Dirkes's avatar

updated 3 years ago

There's a longer story here, but the short version is:

  • I have clearly defined zone loads using the EnergyPlus Lights & OtherEquipment objects. There is ~ZERO envelope load.
  • When I check the E+ output, the zone load differs by 14% from my input values. That's too much.
  • Here are the details. Can someone give me an idea what would cause this variation?
  • Thanks in advance.

image description

Preview: (hide)

Comments

How about a revised question: how can I tell what components contribute to a zone load? In this case, I think I know all of them, but E+ appears to think there are more than I'm aware of (since it's results differ)

Jim Dirkes's avatar Jim Dirkes  ( 4 years ago )

Do you have any infiltration? ZoneInfiltration:DesignFlowRate, ZoneInfiltration:EffectiveLeakageArea, and/or ZoneInfiltration:FlowCoefficient?

ericmartinpe's avatar ericmartinpe  ( 4 years ago )

Good insight! .. but we have no infiltration in the model. We're trying to eliminate influence of the envelope and are also eliminating outdoor air. It's an indoor growing facility and we're focusing on the HVAC exclusively.

Jim Dirkes's avatar Jim Dirkes  ( 4 years ago )