Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Actuate coil capacities with EMS?

asked 2020-11-04 20:18:39 -0600

updated 2020-11-05 09:03:35 -0600

Hi, there,

I need some help on a case where I want to change the cooling and heating coil capacities dynamically under some condition (through EMS program). Systems are fixed-sized in idf, I've tried the Unitary HVAC Design Heating Capacity and Unitary HVAC Design Cooling Capacity, but they're not working. Is it feasible to actuate capacities in E+? Any suggestions?

Thanks!

Test file if you're interested:

  1. With Unitary HVAC Design Capacity actuators
  2. Without actuators
edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
5

answered 2020-11-08 12:25:53 -0600

updated 2020-11-08 12:30:50 -0600

The Unitary HVAC Design Heating Capacity and Unitary HVAC Design Cooling Capacity options that you're using are internal variables -- items that are set once at the beginning of a simulation and don't change (zone floor area, sizing results, etc.). That's why they're not working to dynamically change the coil capacity. To do that, you should instead use actuators. EnergyPlus only has a specific pre-defined list of actuators that you can change -- you don't have the capability to change ANY detail of the model. For cooling coils, it looks like the only actuator available related to capacity is specifically for autosized capacity of single speed DX coils. There don't appear to be any options for actuators related to capacity of heating coils.

There are two workarounds that you could explore to "force" the coils to provide a specific capacity -- the actuators for node setpoints (flow rate, temperatures, and possibly humidity) and the actuator for the performance curve results.

You can read this post for more details.

edit flag offensive delete link more

Comments

Thanks, Aaron. Your answer is very useful!

Yueyue_Zhou's avatar Yueyue_Zhou  ( 2021-01-13 16:17:37 -0600 )edit
1

answered 2020-11-08 11:37:28 -0600

You have to navigate the EDD output file. To get it, you need to place an Output:EnergyManagementSystem object in the IDF file, with at Actuator Availability Dictionary Reporting at least filled with "NotByUniqueKeyNames" to find the actuator type you need

edit flag offensive delete link more

Comments

Thanks, I did so but I didn't find useful actuators so I was wondering whether it's something feasible to do via EMS.

Yueyue_Zhou's avatar Yueyue_Zhou  ( 2021-01-13 16:15:23 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2020-11-04 20:18:39 -0600

Seen: 502 times

Last updated: Jan 13 '21