How to model DX cooling with VAV FPB boxes?

asked 5 years ago

Ranjani's avatar

updated 5 years ago

I am trying to model DX cooling system with VAV FP boxes and they are water-cooled units. I am trying to model the same but I am unable to connect the Cooling Tower to the DX cooling coils.

How can I model this system set up in Open Studio?

Thanks

Preview: (hide)

Comments

@Ranjani are you trying to connect water from the cooling tower to the condenser side of the DX cooling coils (water-cooled DX instead of air-cooled DX)?

Aaron Boranian's avatar Aaron Boranian  ( 5 years ago )

Hi @Aaron Boranian yes that is correct. Is there a way to do it? Thanks

Ranjani's avatar Ranjani  ( 4 years ago )

1 Answer

Sort by » oldest newest most voted
1

answered 5 years ago

sspielman's avatar

I am not sure if you can add DX directly to a VAV box in EnergyPlus, but you could add a ZoneHVAC:WaterToAirHeatPump, which I believe does what you are describing.

See this link... https://bigladdersoftware.com/epx/doc...

Preview: (hide)
link

Comments

If you want it to mimic a VAV box, you could set the fan power of the terminal to zero. You will have to be careful though, because to meet the cooling load in some zones the unit will likely want to recirculate.

sspielman's avatar sspielman  ( 5 years ago )

@sspielman thank you will check it out

Ranjani's avatar Ranjani  ( 4 years ago )