Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

model a water to water heat pump (Equation Fit Approach) [closed]

asked 2015-04-06 13:25:18 -0500

samks123's avatar

updated 2015-07-26 18:12:09 -0500

How can I model a water to water heat pump between a solar collector and water heater.

Is there any example file from energyplus? In addition of the documentation, as I went through it but is not clear to me the steps.

Note: This model is a special case as usually water to water heat pumps are made to perform with ground source heat exchangers.


Update

Hi, Thanks your response!

I have exactly done what you suggested. In this case I decided to connect the wwhp between the solar collectors and water heater (E_Schematic). The diagram, and the idfile is also attached in this email. However, I am getting an error that I cannot figure out. I do not know why it is requesting me or providing me an error of placing a pump at each plant loop. I am trying to avoid the heatExchanger, but if it is required to finish the modelling I will do so.

Please, any suggestions?

Thanks,

SAMBUC:\fakepath\E__Schematic.jpg

C:\fakepath\Solar PVT.jpg

THIS IS THE DIAGRAM C:\fakepath\Solar PVT assissted by a heatpump.jpg

edit retag flag offensive reopen merge delete

Closed for the following reason question is not relevant or outdated by samks123
close date 2015-12-04 17:35:39.964432

Comments

@samks123 I restored your original question and appended your comment which was incorrectly posted in the answers section. In the future when editing/updating your questions please leave the original question so there is context for the answers others give.

MatthewSteen's avatar MatthewSteen  ( 2015-07-05 10:58:41 -0500 )edit

If you provide a schematic naming the EnergyPlus components, including loops and nodes, I will better be able to help you with this. From the images provided, I cannot tell what you are having trouble with.

Also, the HeatExchanger object is very easy to implement.

kwalkerman's avatar kwalkerman  ( 2015-07-06 09:19:29 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
7

answered 2015-06-29 09:36:53 -0500

kwalkerman's avatar

One of the challenges of attaching a water to water heat pump to a solar hot water collector is that currently (Version 8.3.3) the water to water heat pump will only accept a CondenserLoop on the source source side. See this thread on GitHub:

https://github.com/NREL/EnergyPlus/is...

I've been able to mitigate this issue by creative use of the HeatExchanger:FluidToFluid object. You could probably connect your water to water heat pump to the solar connector by putting a heat exchanger just after the solar collector and on the solar collector branch. Put the other side of the heat exchanger just before the water to water heat pump and on the same branch.

edit flag offensive delete link more

Comments

Hey @kwalkerman I am currently doing the same modelling and I would like to provide the schematic diagram of the system. And I had a look of the question you posted in the github, it seems that only condenserLoop is accepted at the source side rather and a PlantLoop which in this case is the Solar collector PlantLoop. I could not sand any pic via comment. May I have your email to send you the schematic diagram? Thanks

nancynanxiaodan's avatar nancynanxiaodan  ( 2015-08-14 11:10:43 -0500 )edit

@nancynaxiaodan: kwalkerman@gmail.com

kwalkerman's avatar kwalkerman  ( 2015-08-14 15:11:08 -0500 )edit

@kwalkerman sent! Thank you very much!

nancynanxiaodan's avatar nancynanxiaodan  ( 2015-08-16 08:41:01 -0500 )edit

Careers

Question Tools

2 followers

Stats

Asked: 2015-04-06 13:25:18 -0500

Seen: 773 times

Last updated: Jul 07 '15