First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Unacceptable heat transfer coefficient values

asked 5 years ago

Amir Tabadkani's avatar

updated 5 years ago

Dear Community,

I have modeled a simple shading system over a single window (venetian blinds) with a glare control on it, but when I output the Hcv on hourly basis, there are some hours that Hcv value is equal to 1000 between the shading system and outer layer of the window!

It seems there is sth wrong within the idf file but I could not find any clue.

Your help is highly appreciated on this issue.

Regards Amir

C:\fakepath\2019-12-22_163028.jpg

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
1

answered 5 years ago

Refer to the E+ engineering documentation on exterior convection where it says:

Note that when the outside environment indicates that it is raining, the exterior surfaces (exposed to wind) are assumed to be wet. The convection coefficient is set to a very high number (1000) and the outside temperature used for the surface will be the wet-bulb temperature. (If you choose to report this variable, you will see 1000 as its value.)

Preview: (hide)
link

Comments

Thanks a lot @shorowit

Amir Tabadkani's avatar Amir Tabadkani  ( 5 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 5 years ago

Seen: 175 times

Last updated: Dec 22 '19