Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Unacceptable heat transfer coefficient values

asked 2019-12-21 23:32:38 -0600

Amir Tabadkani's avatar

updated 2020-01-07 16:49:27 -0600

Dear Community,

I have modeled a simple shading system over a single window (venetian blinds) with a glare control on it, but when I output the Hcv on hourly basis, there are some hours that Hcv value is equal to 1000 between the shading system and outer layer of the window!

It seems there is sth wrong within the idf file but I could not find any clue.

Your help is highly appreciated on this issue.

Regards Amir

C:\fakepath\2019-12-22_163028.jpg

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-12-22 20:46:50 -0600

Refer to the E+ engineering documentation on exterior convection where it says:

Note that when the outside environment indicates that it is raining, the exterior surfaces (exposed to wind) are assumed to be wet. The convection coefficient is set to a very high number (1000) and the outside temperature used for the surface will be the wet-bulb temperature. (If you choose to report this variable, you will see 1000 as its value.)

edit flag offensive delete link more

Comments

Thanks a lot @shorowit

Amir Tabadkani's avatar Amir Tabadkani  ( 2019-12-23 02:28:49 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2019-12-21 23:32:38 -0600

Seen: 159 times

Last updated: Dec 22 '19