Hello,all! I have a question about the simulation of hybrid ventilation using AFN. I built a dedicated outdoor air system. When the system runs, I also set the windows to open by setting the Venting Availability Schedule in the AirflowNetwork:Multizone:Surface. But I didn't define the system in the AirflowNetwork:Distribution. So, is the result correct in this way? I tried to define the system in the AirflowNetwork:Distribution, but I found that I need much information such as the duct and so on. So far, I lack these information. Thanks so mach!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-10-24 12:35:34 -0600

Including distribution in some form would probably lead to a better model of hybrid ventilation, but it is not absolutely necessary to simulate the distribution system to model hybrid ventilation. Assuming that you've set up the model properly, you should be able to see some of what you probably want to see (but not all, since the "multizone" flows and distribution flows can't interact when there's no distribution representation). Actually, even if you do eventually add a representation of distribution, it's a good idea to see if the model you already have works as desired. As you say, building out the distribution model is a non-trivial time investment and requires additional information.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2019-10-23 03:42:40 -0600

Seen: 197 times

Last updated: Oct 24 '19