Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
5

VERY high latent load autosizing

asked 2019-10-02 06:38:10 -0500

Jim Dirkes's avatar

updated 2019-10-02 13:20:02 -0500

I'm modeling an indoor greenhouse. The watering of plants creates very high internal latent load. Concurrent with that, the plant evapotranspiration causes a sensible cooling effect. Overall, it's a very unusual sizing problem - at least I think it is for E+ autosizing.

Regardless, E+ is NOT controlling humidity very well for the chilled water system I've defined :(

Can you provide any tips for proper setup for autosizing in this situation?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2020-04-29 06:36:19 -0500

Jim Dirkes's avatar

After more experience.... E+ does NOT autosize latent loads well. Manual sizing works well, but requires preparation of a load calculation and equipment sizes :(

edit flag offensive delete link more

Comments

ericringold's avatar ericringold  ( 2020-04-30 08:23:31 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2019-10-02 06:38:10 -0500

Seen: 527 times

Last updated: Apr 29 '20