VERY high latent load autosizing

asked 2019-10-02 06:38:10 -0600

Jim Dirkes's avatar

updated 2019-10-02 13:20:02 -0600

I'm modeling an indoor greenhouse. The watering of plants creates very high internal latent load. Concurrent with that, the plant evapotranspiration causes a sensible cooling effect. Overall, it's a very unusual sizing problem - at least I think it is for E+ autosizing.

Regardless, E+ is NOT controlling humidity very well for the chilled water system I've defined :(

Can you provide any tips for proper setup for autosizing in this situation?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2020-04-29 06:36:19 -0600

Jim Dirkes's avatar

After more experience.... E+ does NOT autosize latent loads well. Manual sizing works well, but requires preparation of a load calculation and equipment sizes :(

edit flag offensive delete link more

Comments

ericringold's avatar ericringold  ( 2020-04-30 08:23:31 -0600 )edit