Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Any way to input MRT in CBE Thermal Comfort Calculator?

asked 2019-07-29 08:21:25 -0600

katsuya.obara's avatar

I am trying to study the effect of solar radiation to thermal comfort using CBE Thermal Comfort Calculator.
I used SolarCal function and got the delta MRT as below.
However, this MRT is not reflected even pushing Adjust MRT.
Also, I cannot find any interface to input MRT even though it is shown in the interface in [help page] (http://comfort.cbe.berkeley.edu/stati...) as below.
Can anyone know how I can reflect the calculation result from SolarCal?

image description

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
6

answered 2019-07-30 06:28:22 -0600

If you click on the EN-15251 button in the top right-hand corner of the CBE Thermal Comfort Tool then you have the option of entering air temperature and mean radiant temperature separately. Alternatively, you can use Appendix C of ASHRAE 55 to calculate the operative temperature based on the air temperature, mean radiant temperature, and relative air speed. Appendix C does note that in most cases, the relative air speed and/or the difference between mean radiant temperature and air temperature is small. In this case, the operative temperature can be estimated as the mean value of the air temperature and the mean radiant temperature.

image description

image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2019-07-29 08:21:25 -0600

Seen: 750 times

Last updated: Jul 30 '19