Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Openstudio Baseline Chiller COP

asked 5 years ago

updated 5 years ago

I am confused about which parameter I should use when deciding the baseline chiller COP through the EnergyPluse report. Should I use (a) cooling coils: Nominal total Capacity or use (b) Annual and peak values - Cooling: Cooling Maximum Value (CoolingCoils:PlantLoopCoolingDemand). The value from option (b) for my model is around 20% smaller than the value from option (a). That is why I got confused about which value to use.

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
1

answered 5 years ago

Are you interested in average chiller COP from the annual simulation or chiller COP at rated conditions?

Chiller values are listed under the Central Plant table in the Equipment Summary report. There are IPLV values and nominal efficiency. If you want run time efficiency, use the Chiller COP Output:Variable.

Preview: (hide)
link

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 5 years ago

Seen: 345 times

Last updated: Jul 11 '19