Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Openstudio Baseline Chiller COP

asked 2019-07-10 09:57:55 -0500

updated 2019-07-14 12:40:24 -0500

I am confused about which parameter I should use when deciding the baseline chiller COP through the EnergyPluse report. Should I use (a) cooling coils: Nominal total Capacity or use (b) Annual and peak values - Cooling: Cooling Maximum Value (CoolingCoils:PlantLoopCoolingDemand). The value from option (b) for my model is around 20% smaller than the value from option (a). That is why I got confused about which value to use.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-07-11 12:48:51 -0500

Are you interested in average chiller COP from the annual simulation or chiller COP at rated conditions?

Chiller values are listed under the Central Plant table in the Equipment Summary report. There are IPLV values and nominal efficiency. If you want run time efficiency, use the Chiller COP Output:Variable.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2019-07-10 09:57:55 -0500

Seen: 314 times

Last updated: Jul 11 '19