Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

AirFlowNetwork control

asked 2019-07-05 07:44:17 -0600

Franci19's avatar

updated 2019-07-06 09:07:04 -0600

Hello everybody, I'm new here and in the use of EnergyPlus! I have already looked for an answer in existing issues but I couldn't find it. I hope my question is not useless.

I'm implementing the ASHRAE Small Office in EnergyPlus v8.0 adding an AirFlowNetwork for an accurate opening of the windows. I see that in AirFlowNetwork:SimulationControl is possible to select different AirFlowNetwork Controls (MultiZoneWithDistribution, MultiZoneWithoutDistribution, MultiZoneWithDistributionOnlyDuringFanOperation or NoMultiZoneOrDistribution) that allow the calculation of the air exchanges between zones.

The problem is that I would like to implement a new model of window opening leaving the previous setting for infiltration (in the base model the infiltrations are modeled with ZoneInfiltration:DesignFlowRate) in order to evaluate the only window opening influence. I see that MultiZoneWithDistributionOnlyDuringFanOperation is the only control that allows the ZoneInfiltration to run but it performs the MultiZone calculation only during HVAC fan operation.

Does this mean that it considers the influence of window opening only during HVAC fan operation? I would like to consider it during every timestep. Is there another a way?

Thank you everybody!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-07-05 20:00:24 -0600

If I understand what you're asking correctly, then yes, I think it is the case that the AirflowNetwork window elements won't have an impact when the fans aren't operating. To get what you want you'll have to replace your previous infiltration objects with enough (AirflowNetwork) leakage to get about the infiltration you had before.

There are a lot of reasons the infiltration objects and AirflowNetwork are kept apart, but at a high level those infiltration objects are a load (outside air that needs conditioning) while AirflowNetwork is balancing inflows (which we can consider as loads) and outflows (not loads). That's glossing over a whole bunch of details, but that's the basic idea.

edit flag offensive delete link more

Comments

Also, why 8.0? There have been a lot of bug fixes since then.

Jason DeGraw's avatar Jason DeGraw  ( 2019-07-09 08:51:26 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2019-07-05 07:44:17 -0600

Seen: 694 times

Last updated: Jul 05 '19