LoadProfile:Plant in AirLoopHVAC

asked 2019-06-19 09:07:13 -0600

updated 2019-06-19 09:07:54 -0600

Is it possible to use a LoadProfile:Plant object on the demand side of an AirLoopHVAC, to model the air flow requirements, instead of connecting the plant to a thermal zone?

In the InputOutput Reference they only mention the case of coupling it with a water loop, but there is no mention of air loops. Anyone tried it? Thanks

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2019-06-19 12:16:41 -0600

The plant load profile must be connected to a water loop using the inlet/outlet node fields and is also only called by the (water) plant. For these reasons this object cannot be connected to an air loop.