Can I use minisplit as a cooling equipment along with radiant hot water (boiler?) I can't figure out how to set up a system with hot water radiant and minisplit for cooling?image description

image description

As you can see there is still a cooling load despite the error messages?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2019-06-05 10:36:58 -0600

BEopt cannot model multiple pieces of equipment that both provide heating (or cooling). Since BEopt assumes that the mini-split will be providing both, it cannot be combined with a boiler. If you have a mini-split selected and then try to select a boiler (or vice versa), it will automatically deselect the other option to prevent two pieces of equipment providing heating.

That said, you could use BEopt to do two separate runs -- one with a mini-split and one with a boiler/AC -- and then combine the results using the cooling energy from the mini-split run and the heating energy from the boiler run.

edit flag offensive delete link more

Comments

Thanks. It would be nice to be able to show minisplit for cooling only, as this is quite often a specified application.

et's avatar et  ( 2019-06-05 10:41:51 -0600 )edit

so in my final output everything is identified as Point 1, Point 2, Point 3,, Point 4, Point 5, but I can't figure out ow cases are indicated as Points... which case is which point?

et's avatar et  ( 2019-06-05 10:52:46 -0600 )edit
2

I assume you are in the "Parametric" mode. You can switch to the "Design" mode and then right click on the "My Design" tab. There you can change the name of a single scenario and also create a new design with a proper name. When you run the analysis, the outputs will be shown based on the names you have assigned as opposed to Point 1, 2, etc. This can be a little bit inconvenient when there are multiple design scenarios but I think this is the only way to have the actual names on the output graphs.

Ehsank's avatar Ehsank  ( 2019-06-06 09:21:33 -0600 )edit