Design flow rate and pressure difference (50Pa?)

asked 2019-06-04 08:29:58 -0600

NCB's avatar

I'm trying to define in OpenStudio Space Infiltration Design Flow rate, by using a design flow rate parameters of a buildings similar to my study cases. My reference data have the results with 50Pa of pressure difference. I read the engineering reference and don't see any limit to the pressure use for that. (For the case of Effective Leakage area, it is well defined that should be 4Pa) Can i use a flow rate of 50Pa for the simulation? I hope anyone can help me,

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2019-06-04 10:31:12 -0600

The OpenStudio Space Infiltration Design Flow rate input is assumed to be at natural pressure. So you need to convert the infiltration rate at 50 Pa to the rate at natural pressure (~4 Pa).

See the answer to "how to set air infiltration under 50 pa pressure" on the forum. There is a table for residential projects to convert ACH50 to ACHnat.

Otherwise, you can calculate it from Q_delta_P = C*(delta_P)^n, where Q is the infiltration rate at pressure differential delta_P, n = 0.65, and C is the flow coefficient. Given your known infiltration Q at 50 Pa, calculate C. Then change delta_P to natural pressure (~4 Pa) and calculate Q.

edit flag offensive delete link more

Comments

thank you so much!!

NCB's avatar NCB  ( 2019-06-04 10:33:46 -0600 )edit