Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

ideal air load measure error

asked 2019-05-24 10:35:40 -0500

Mamak's avatar

updated 2019-05-27 15:27:34 -0500

Guys, In the "Ideal load option" measure of the open studio, I have chose "use individual zone design out door air" for out door specification...Than I have defined "design specification outdoor air object " for each zone...but when I run the simulation there is this error:

Error: Unable to find design specification outdoor air for zone 2nd floor bedrooms. Please specify a design specification outdoor air object for the zone, or select None for Outdoor Air Specification.

any idea what is the problem?

Thanks

edit retag flag offensive close merge delete

Comments

design specification outdoor air objects get defined at the space or space type level, not at the zone. The error is pretty clear - the model is missing the object. Can you check both your space and space type design specification outdoor air object fields and post a link to the model if you are still getting the error?

mdahlhausen's avatar mdahlhausen  ( 2019-05-24 10:50:59 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
0

answered 2019-05-24 18:18:34 -0500

The issue is that your model does not contain design day objects. If the model does not include design days, then the .osm to .idf translator does not create zone sizing objects which contain the reference to the design specification outdoor air objects for your zones.

I've updated the measure on BCL to throw an error when design days are missing before it checks the zone sizing objects for the design specification outdoor air.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2019-05-24 10:35:40 -0500

Seen: 139 times

Last updated: May 24 '19