Which is the proper "ZoneInfiltration:DesignFlowRate" value, with ideal air loads?

asked 10 years ago

Antop's avatar

updated 9 years ago

I am setting two models without HVAC system (residential and office). I am using the ideal air load.

  • In your opinion, which is the proper value of space infiltration (in term of ACH) I have to use?
  • With ideal loads is there already mechanical ventilation?
  • Do I have to consider a combination between mechanical ventilation and infiltration?
Preview: (hide)

Comments

1

I believe that DesignFlowRates can be defined independently of the IdealAirLoads system. The IdealAirLoads system is driven by thermostats and should take into account any infiltration that occurs.

OS-user-AT's avatar OS-user-AT  ( 9 years ago )

1 Answer

Sort by » oldest newest most voted
5

answered 9 years ago

hongtz's avatar

updated 9 years ago

Infiltration varies significantly among buildings and time. PNNL report PNNL-18898, Infiltration Modeling Guidelines for Commercial Building Energy Analysis (pdf), is a good reference.

Preview: (hide)
link

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer