Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Default cooling system settings

asked 2019-05-10 08:37:37 -0600

Ivanita's avatar

updated 2019-05-10 14:41:57 -0600

I am a new user of E+. I performed some simulations (using the default setting for most items) and noticed that the default cooling system is district cooling system. I would like to ask

1) how can I check the settings, e.g. COP, of the district cooling system? Can I check the settings by using IDF editor? 2) How can i change to other systems?

Thanks.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2019-05-10 15:13:43 -0600

updated 2019-05-10 15:15:51 -0600

District cooling "has" a COP of 1. It mimics the real life scenario where you receive chilled water from a central plant. It basically a constant sink of capacity that you are billed for by the unit of energy. Therefore, you can only specify the maximum capacity of the object, not the performance.

You can replace the District Cooling for a Chiller:ConstantCOP object, but you would also need to create a condenser water loop with a cooling tower. You will connect the Chilled Water Inlet Node Name to the inlet node of the Distric cooling object and the Chilled Water Outlet Node Name to the outlet node of the object.

You can read more about the Chiller:ConstantCOP here.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2019-05-10 08:37:37 -0600

Seen: 191 times

Last updated: May 10 '19