Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Strange behavior of cooling, heating energy consumption and Blinds operation

asked 2015-03-20 06:51:30 -0600

Waseem's avatar

updated 2015-07-11 10:41:40 -0600

Hi All,

I am trying to model blinds in EnergyPlus, I have setup Daylighting:Controls and have a schedule to operate blinds. However, when I try to simulate my building it gives readings that lighting energy increases when there was blinds (make sense) but it also gives results that heating and cooling energy consumption increase when there was blinds (This does not make sense to me). The blinds should be blocking solar gains and therefore there should be reduction in cooling energy, on the other hand it will also reduce heat loss and hence reduction in heating energy consumption.

I may be missing some small point but unable to figure it out at the moment. Any ideas? The location for weather file is UK and there is only one south facing window.

Thanks

edit retag flag offensive close merge delete

Comments

2

Less solar gains can result in increased heating. On the other hand it should reduce cooling. However, due to decreased available daylight your internal gains from artificial lighting are increasing, affecting both heating and cooling. Former should be decreased while latter should be increased. It can be difficult to find a balance between all these phenomena. In addition to this, a building thermal mass also affects cooling and heating requirements.

Ivan Korolija's avatar Ivan Korolija  ( 2015-03-20 06:59:37 -0600 )edit

Thanks, I agree. I missed the point before posting this question. I should have plotted lighting gains as well.

Waseem's avatar Waseem  ( 2015-03-20 07:22:59 -0600 )edit
3

This reminds me of a lengthy and interesting discussion on the Yahoo EnergyPlus group last year. If the lighting load doesn't entirely account for the increase then you might take a look at that thread. https://groups.yahoo.com/neo/groups/E...

Jamie Bull's avatar Jamie Bull  ( 2015-03-20 09:30:30 -0600 )edit
1
Waseem's avatar Waseem  ( 2015-03-23 05:34:38 -0600 )edit

@Ivan Korolija Please repost your comment as an answer to this question so that is no longer shows as "unanswered". Thanks.

MJWitte's avatar MJWitte  ( 2015-10-15 13:56:12 -0600 )edit

2 Answers

Sort by ยป oldest newest most voted
3

answered 2015-10-15 14:16:49 -0600

Ivan Korolija's avatar

Less solar gains can result in increased heating. On the other hand it should reduce cooling. However, due to decreased available daylight your internal gains from artificial lighting are increasing, affecting both heating and cooling. Former should be decreased while latter should be increased. It can be difficult to find a balance between all these phenomena. In addition to this, a building thermal mass also affects cooling and heating requirements.

edit flag offensive delete link more

Comments

And any solar absorbed by the blinds will become an instant heat gain compare to solar that is absorbed in a wall or floor which results in a delayed load.

MJWitte's avatar MJWitte  ( 2015-10-20 15:48:42 -0600 )edit
2

answered 2015-10-15 15:30:59 -0600

Archmage's avatar

Another point to consider is that lighting power also serves as reheat. If the HVAC system is doing latent control and has reheat, it can happen that reductions in lighting lead to increased heating because the reheat coils need to work more.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2015-03-20 06:51:30 -0600

Seen: 360 times

Last updated: Oct 15 '15