** Warning ** GetDensityGlycol: Temperature is out of range (too low) for fluid [WATER] density **
** ~~~ ** ..Called From:CalcWatertoWaterHPHeating,Temperature=[-10.99], supplied data range=[0.00,100.00]
** ~~~ ** Environment=SHANGHAI ANN HTG 99.6% CONDNS DB, at Simulation time=01/21 00:00 - 00:15
** Warning ** GetSpecificHeatGlycol: Temperature is out of range (too low) for fluid [WATER] specific heat supplied values **
** ~~~ ** ..Called From:CalcWatertoWaterHPHeating,Temperature=[-10.99], supplied data range=[0.00,125.00]
** ~~~ ** Environment=SHANGHAI ANN HTG 99.6% CONDNS DB, at Simulation time=01/21 00:00 - 00:15
** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for DOAS SYSTEM-Y, at RUNPERIOD1, 07/11 20:30 - 20:35
The warnings show that the water temperature is -10.99 C. This is obviously wrong and something in the simulation is causing the water-to-water heating coil to turn on when the plant is unable to sufficiently heat the water loop. To help determine the cause add:
Output:Diagnostics,ReportDuringWarmup;
Then add Output:Variable reports for the plant loop water inlet and outlet nodes, the equipment performance reports for the plant loop equipment, and the water-to-water coil reports for air and water side nodes.
After the simulation is complete open the variables report and review the performance of the HVAC and plant. I suspect you will find that the plant is not operating as expected during the warmup period and the plant temperatures are too low for some reason.