Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Water heater consumption (kWh)

asked 2019-02-22 13:59:14 -0600

VanessaCosta's avatar

updated 2019-02-22 19:52:16 -0600

Hi, I'm trying to simulate a stratified water heater for São Paulo-Brazil .epw and find out the consumption of the heater (kWh) for each month. I'm using a heater of 6000W capacity, with a patter of bath 40minutes per day (4l/min). I got the consumption from the Table Report and it is too high (The usual is maximum of 90kWh for a month). I converted J to kWh and got this:

WATER HEATER TOTAL DEMAND HEAT TRANSFER ENERGY [J](kWh) WATER HEATER HEAT LOSS ENERGY [J]   (kWh)
January          482239000.00                                     133.96    -79534413.60                                           -22.09
February             443646000.00                                     123.24    -73541655.60                                           -20.43
March            538367000.00                                     149.55    -85841829.00                                           -23.84
April                    550458000.00                                     152.91    -94792808.10                                           -26.33
May                  600509000.00                                     166.81    -105807662.30                                          -29.39
June                     580653000.00                                     161.29    -102193879.20                                          -28.39
July                     612884000.00                                     170.25    -108955406.70                                          -30.27
August           591676000.00                                       164.35  -103599575.70                                          -28.78
September    556954000.00                                     154.71    -96280359.00                                           -26.74
October          578996000.00                                     160.83    -99992914.30                                           -27.78
November             543994000.00                                     151.11    -93088050.10                                           -25.86
December             540370000.00                                     150.10    -89565130.60                                           -24.88

The temperature of the tank outlet looks fine. I dont know if I'm using the wrong output object to obtain the consumption results or if there is a mistake in my .idf. I'm senting a link if somebody want to give me a little help here.

https://www.dropbox.com/sh/or7f0yk7p6... Thanks!

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
0

answered 2019-02-22 18:10:07 -0600

updated 2019-02-22 19:49:06 -0600

You have what appears to be a large loss coefficient.

WaterHeater:Stratified,
    Storage Tank Stratified, !- Name
    0.15,                    !- Node 1 Additional Loss Coefficient {W/K}
    0.1;                     !- Node 6 Additional Loss Coefficient {W/K}

10% to 15% in losses seems high to me but I am not an expert in water tanks. Try decreasing these losses and see if the tank acts more like you would expect (e.g.,divide losses by 10 to 0.015 or 0.01 W/K)

edit flag offensive delete link more

Comments

Hi! I tried that but it didn't change much. The demand is still too high for month (january that is summer, for exemplo, 112kWh).

VanessaCosta's avatar VanessaCosta  ( 2019-02-22 19:17:44 -0600 )edit

Can you clean up that table in your description so I can see it better? The losses are about an order of magnitude lower than the heat transfer (so heat transfer should be predominant). I expect that you just don't understand the results. Let's narrow this down.

  • Set the losses to 0 until you figure this out.
  • Compare the water draw schedule (profile) to the heat transfer (profile) to see if they match up
rraustad's avatar rraustad  ( 2019-02-22 19:23:47 -0600 )edit

WATER HEATER TOTAL DEMAND HEAT TRANSFER ENERGY [W] January 130898.61 February 120408.61 March 146261.11 April 149282.78 May 162756.11 June 157383.06 July 166070.83 August 160386.94 September 151023.61 October 157001.39 November 147546.67 December 146673.90

VanessaCosta's avatar VanessaCosta  ( 2019-02-22 19:55:03 -0600 )edit

WATER HEATER HEAT LOSS ENERGY [W]
January -19.04 February -17.60 March -20.55 April -22.69 May -25.32 June -24.46 July -26.08 August -24.80 September -23.04 October -23.93 November -22.28 December -21.44

VanessaCosta's avatar VanessaCosta  ( 2019-02-22 20:01:41 -0600 )edit

Something is wrong. You have a 6 kW water heater with a 130898 W demand for January. We have to figure out what that means before proceeding. Is that W or kWh?

rraustad's avatar rraustad  ( 2019-02-22 20:03:16 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2019-02-22 13:59:14 -0600

Seen: 272 times

Last updated: Feb 22 '19