Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Is it feasible that in CHW Cooling coil, design coil load is much greater than Nominal capacity?

asked 2019-01-18 23:12:45 -0600

Smruti's avatar

updated 2019-01-21 15:02:13 -0600

Hi,

I have attached the OSM file and the eplus output file. I don't understand where I have made mistake.

  • The cooling coil design load is 2837396 W whereas, its nominal capacity is 1775951 W
  • The cooling tower has less wattage (2682661 W) than electric chiller (2837348 W).
  • The comfort parameter is never met through out the year.

Please help.

Regards, Smruti

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2019-01-22 07:15:45 -0600

Smruti's avatar

I have rectified the problem my self.

  • The problem was related to the sizing factors. I gave a global sizing factor of 1.25 for cooling equipment as well as 1.25 for chiller. This made the chiller having more wattage than the cooling tower.

  • The comfort parameters are satisfied after I changed the default setting (like loop exit temperature and loop temperature difference)about condenser and chiller loops in open studio.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2019-01-18 23:12:45 -0600

Seen: 157 times

Last updated: Jan 22 '19