Why 'Zone Ideal Loads Zone Total Heating Energy', 'Zone Ideal Loads Zone Total Cooling Energy' don't appear in my variables

asked 6 years ago

cmgs's avatar

updated 6 years ago

i turned ideal air loads on and created schedules for both cooling and heating thermostats

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
0

answered 6 years ago

saeranv's avatar

The Ideal Loads are modeled as if they are provided by a district heating/cooling plant with no sizing constraints. So it should be reported under the DistrictHeating and DistrictCooling Output variables.