Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Error in Beopt 2.8 when running ASHP in cold climate

asked 2018-11-10 22:10:30 -0600

lolo's avatar

updated 2018-11-12 13:25:51 -0600

11/10/2018 8:41 PM: 092.xml: Error: * Fatal * Program terminates due to above conditions. 11/10/2018 8:41 PM: 094.xml: Error: * Severe * DualSetPointWithDeadBand: Unanticipated combination of heating and cooling loads - report to EnergyPlus Development Team 11/10/2018 8:41 PM: 094.xml: Error: * ~~~ * occurs in Zone=FINISHEDBASEMENT_1 During Warmup, Environment=PLANT DD, at Simulation time=01/01 00:00 - 01:00 11/10/2018 8:41 PM: 094.xml: Error: * ~~~ * LoadToHeatingSetPoint=NAN, LoadToCoolingSetPoint=NAN 11/10/2018 8:41 PM: 094.xml: Error: * ~~~ * Zone Heating Set-point=21.67 11/10/2018 8:41 PM: 094.xml: Error: * ~~~ * Zone Cooling Set-point=24.44 11/10/2018 8:41 PM: 094.xml: Error: * ~~~ * Zone TempDepZnLd=209.18 11/10/2018 8:41 PM: 094.xml: Error: * ~~~ * Zone TempIndZnLd=NAN 11/10/2018 8:41 PM: 094.xml: Error: * ~~~ * Zone ThermostatSetPoint=0.00

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2018-11-12 11:33:14 -0600

This is caused by an EnergyPlus bug in the Kiva foundation model that was fairly recently fixed for EnergyPlus v9. We don't yet have a release of BEopt that includes the new EnergyPlus version.

For the time being, the only workaround is to grab the EnergyPlus IDF from BEopt, transition it to EnergyPlus v9, and run the file manually in EnergyPlus.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2018-11-10 22:10:30 -0600

Seen: 344 times

Last updated: Nov 12 '18