Energyplus : Calculation of cooling coil design UA failed for coil CHW CLG COIL

asked 6 years ago

Siv's avatar

updated 6 years ago

Can anyone please tell me why this error might appear ?

Calculation of cooling coil design UA failed for coil CHW CLG COIL Bad starting values for UA * ~~~ * Coil design UA set to 49770.080623 [W/C]

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
4

answered 6 years ago

updated 5 years ago

This is likely caused by a discrepancy in the Coil:Cooling:Water object design temperature/humidity ratio, plant water temperature (Sizing:Plant), Sizing:System supply air temperature (assuming an air loop coil) or Sizing:Zone supply air temperature (assuming a zone coil) inputs. Feel free to ask more questions on this subject.