Zero "Zone Air Terminal Outdoor Air Volume Flow Rate" on design days
Hello All, Although I've set outdoor air method in DesignSpecification:OutdoorAir and I used it in Controller:MechanicalVentilation, Sizing:Zone, and AIRTERMINAL:SINGLEDUCT:VAV:REHEAT, the Zone Air Terminal Outdoor Air Volume Flow Rate on my design days are zero. I am using autosized hvac calculation. Any insight would be appreciated.
Verify that occ schedules are not 0 for the hours for the design runs.
Actually there are internal heat gains from people, lights and so on. And indoor temperature is much higher than the cooling setpoint on summer design day.
Do you have any airflow at all from the system?
How can I check it? Actually on the same day (i.e. summer design day) in the annual simulation run, the "Zone Air Terminal Outdoor Air Volume Flow Rate" is not zero.