Ice Thermal Storage Control OpenStudio

asked 2018-09-11 14:37:30 -0600

madisonlikins's avatar

updated 2018-09-11 18:52:28 -0600

I am currently working on modeling an ice thermal storage unit in OpenStudio. During off peak hours, I want the tank to charge using a dedicated chiller, while a main chiller serves the building. During peak hours, I want both chillers off and the tank to discharge and serve the building. I have attached a diagram of my system below. My system is running, but the charging and discharging rates are not expected and do not make sense (picture posted below). I have the setpoint managers and availability managers operating the same way as the eplus example file "IceStorage-Parallel" but with extremely different trends in the output. Does anyone have any insight on how to better control the charging and discharging of an ice storage system within OpenStudio?

edit retag flag offensive close merge delete

Comments

I don't see any pictures, probably because you didn't have enough karma, but now with two upvotes you should be able to edit your post to include the pictures.

Julien Marrec's avatar Julien Marrec  ( 2018-09-12 02:15:32 -0600 )edit