Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Heating equipment sizing and people load

asked 2018-07-31 13:39:06 -0600

S's avatar

updated 2018-08-06 07:55:04 -0600

Hello All, Is the internal heat gain from occupants taken into account for heating equipment sizing? Thanks

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2018-08-01 02:53:41 -0600

Marco Furlani's avatar

Hi, normally not accounting heat gain from people for heating sizing (so building equipment can met peak heating demand also when it is unoccupied). But if yuo want to take in consideration a base gain of people in some circustances (i.e. any constant occupation for cerain particular building type) you can revise the schedule:compact of the people occupancy and improve your specific schedule (period and fraction) for the WinterDesignDay (that normally is set to zero). Furthermore, check plant and/or equipment oversizing factor for an accurate evaluation between sizing and peak heat demand.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-07-31 13:39:06 -0600

Seen: 123 times

Last updated: Aug 01 '18