Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How to model thin metal material layer

asked 2018-07-29 06:21:26 -0600

manish kumar's avatar

updated 2018-08-05 08:56:52 -0600

in i/p o/p reference object material thickness(x>3mm) and k(<5w/m-k) is to be filled but if i want x<3mm and k=200 then how i do so

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-08-01 13:56:26 -0600

As it says in the Input Output Reference, modeling thin highly conductive layers is not recommended. They can cause instabilities in the heat transfer model. Typically, such layers have little or no impact on the heat transfer or capacitance, only on the surface properties for solar and thermal absorptance. So you can

  1. Model the layer as-is and see if any errors results.
  2. Omit this layer
  3. Omit this layer and change the absorptance properties of the next materiel layer to act as if it were coated with metal.
edit flag offensive delete link more