Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

How can i fix supply air temperature for VRF in EnergyPlus?

asked 2018-07-03 02:31:49 -0500

joooon's avatar

updated 2018-07-03 02:36:51 -0500

Hi! Now I am modelling a building equipped with VRF system. Even though generally supply air temperature of Japanese VRF is higher by 10 degrees Celcius than zone setpoint temperature, the model now i am modelling supplies in approximately 41 degrees Celcius. so i want to fix the VRF supply air temperature as 32 degrees celcius. how can i do this?

i've already tried SetpointManager:FollowSystemNodeTemperature. but it didn't work. additionally, SetpointManager:Warmest and SetpointManager:WarmestTemperatureFlow don't work for VRF systems

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2018-07-03 17:55:56 -0500

Set the Zone Heating Design Supply Air Temperature field in your Sizing:Zone objects to 32°C.

edit flag offensive delete link more

Comments

thank you for your answer! i will try this! :)

joooon's avatar joooon  ( 2018-07-04 05:32:32 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

Stats

Asked: 2018-07-03 02:31:49 -0500

Seen: 230 times

Last updated: Jul 03 '18