How can i fix supply air temperature for VRF in EnergyPlus?

asked 6 years ago

joooon's avatar

updated 6 years ago

Hi! Now I am modelling a building equipped with VRF system. Even though generally supply air temperature of Japanese VRF is higher by 10 degrees Celcius than zone setpoint temperature, the model now i am modelling supplies in approximately 41 degrees Celcius. so i want to fix the VRF supply air temperature as 32 degrees celcius. how can i do this?

i've already tried SetpointManager:FollowSystemNodeTemperature. but it didn't work. additionally, SetpointManager:Warmest and SetpointManager:WarmestTemperatureFlow don't work for VRF systems

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
2

answered 6 years ago

Set the Zone Heating Design Supply Air Temperature field in your Sizing:Zone objects to 32°C.

Preview: (hide)
link

Comments

thank you for your answer! i will try this! :)

joooon's avatar joooon  ( 6 years ago )