Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

The annual peak cooling value includes sensible and latent cooling?

asked 2018-06-13 12:06:03 -0600

Prinz Qwert's avatar

updated 2018-06-28 17:02:30 -0600

Hello!

I am wondering if the 'Annual and Peak Values - Cooling' in the 'Annual Building Utility Performance Summary' includes the latent and sensible cooling?

Thank you!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-06-19 12:46:31 -0600

Yes, the values in this table include both sensible and latent cooling coil loads.

Just to be clear, 'Annual and Peak Values - Cooling' is a subtable of the Energy Meters (EnergyMeters) report, not ABUPS. Each of the row labels in this report is a meter name, for example CoolingCoils:PlantLoopCoolingDemand. The output variables which are connected to every meter are documented in the meter details (mtd) output file. For example, from the 5ZoneAirCooled example file:

For Meter=CoolingCoils:PlantLoopCoolingDemand [J], ResourceType=PlantLoopCoolingDemand, EndUse=CoolingCoils, contents are:
 OA COOLING COIL 1:Cooling Coil Source Side Heat Transfer Energy
 MAIN COOLING COIL 1:Cooling Coil Source Side Heat Transfer Energy

Output variables are defined in the Input Output Reference:

Cooling Coil Source Side Heat Transfer Energy [J] This is the energy extracted from the chilled water serving the coil, in Joules.

The important thing to understand is that this is the total load served by chilled water (only) cooling coils, so it includes sensible and latent plus other system effects such as fan heat, outdoor air loads, heat recovery etc.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-06-13 12:06:03 -0600

Seen: 189 times

Last updated: Jun 19 '18