Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Can energyplus model Airflow network with VAV supply fan?

asked 2018-04-12 15:59:47 -0600

TomB's avatar

The EnergyPlus documentation seems to say that an Airflow Network requires a constant volume supply fan.

image description

And yet, there is an example file (v8.8) with a variable air volume supply fan in an Airflow Network ..?

image description

Am I misreading the limitations, or is the documentation out of date?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2018-04-13 10:00:50 -0600

updated 2018-04-13 10:11:29 -0600

Yes; the input/output documentation is out of date.

This section in the engineering reference describes the calculation procedure for AirflowNetwork with a Fan:VariableVolume and AirTerminal:SingleDuct:VAV:Reheat terminals.

You can also run the example file and verify variable airflow through the air system using the System Node Mass Flow Rate output variable as well as AirflowNetwork operation with the AFN Linkage Node 1 to Node 2 Volume Flow Rate variable.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-04-12 15:59:47 -0600

Seen: 200 times

Last updated: Apr 13 '18