Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Temperature and humidity in design builder

asked 2018-03-09 06:57:58 -0600

andreea's avatar

updated 2018-03-11 10:56:41 -0600

i have a building with heated floor and when i run the simulations the temperature and humidity are not constant in the same summer/winter week design. so in the summer i have temperatures between 20-40 deg and a humidity between 40-70% and in the winter the temperatures are between 19-20 deg and humidity between 9-15%

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
4

answered 2018-03-09 10:40:43 -0600

mikesweeney's avatar

it sounds like you have a heating setpoint of 20, but either no cooling setpoint or no cooling equipment assigned to your zones, which means during cooling season temperatures will float between 20-40. likewise, if you don't have any cooling equipment there's no way to control humidity during cooling season. if you put cooling equipment into your zones, you'll also have to assign a humidistat (and if you're using an air loop, use a humidity-related setpoint manager) in order to control for humidity.

edit flag offensive delete link more
2

answered 2018-03-13 05:26:47 -0600

andreea's avatar

Thanks for the reply! For the project I have a heating and cooling system in the floor and the heat part I have in the program, but I do not know how to add the cooling part and I think this is the main cause of the big temperature differences.

edit flag offensive delete link more

Comments

does the floor cooling system have chilled water? if so, you'd need to have a chilled water plant connected to it. if you send me the designbuilder model i can take a look.

mikesweeney's avatar mikesweeney  ( 2018-03-14 08:41:06 -0600 )edit
1

yes it has, but the idea is that it does not let me put the cooling system in the floor and also the underfloor heating (pipes). so I put the cooling system in the ceiling, although that's not what I need and anyway it generates too many errors. I would like to send the model but I do not know how, so if you have an ideea i will do it

andreea's avatar andreea  ( 2018-03-14 09:47:11 -0600 )edit

i'm not sure about cooling in the floor, but designbuilder 5.2 has a "radiant surface" component you could try. or look here for advice on how to model chilled ceiling. you may then have to do a workaround and/or some post processing to get it to represent the differences in stratification properly.

mikesweeney's avatar mikesweeney  ( 2018-03-15 09:53:05 -0600 )edit
1

thank you for your help!

andreea's avatar andreea  ( 2018-03-16 02:51:07 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-03-09 06:57:58 -0600

Seen: 466 times

Last updated: Mar 13 '18